December 22, 2025Dec 22 comment_621 Hi Everyone I’m working on an L-shaped RC building where a movement joint is required, primarily to accommodate thermal and shrinkage movements in RC flat slab. The two wings meet at a re-entrant corner, with the left wing skewed relative to the right wing by approx. 54°.The proposed solution is to provide a movement joint through the slabs, with Ancon ESDQ (available in the UK; lateral, rotational and longitudinal movement allowed)dowels across the joint. The design intent is:Transfer vertical shear only across the jointNo transfer of in-plane axial force, shear, or momentAllow longitudinal, lateral, and rotational movement across the jointDowels generally perpendicular to the joint lineWith respect to wind-induced differential deflection between the two wings:Is the correct design approach to:determine the maximum relative horizontal displacement between the two structures at the joint (from SLS wind combinations),combine this with thermal, shrinkage, and construction tolerances, andthen specify a required movement capacity for the dowels (axial/lateral, as applicable) to ensure the system does not bind or lock up?Many thanks Report
Tuesday at 09:56 AM4 days comment_640 The approach is broadly right, but I’d resolve the SLS wind relative movement into components parallel and perpendicular to the joint and combine them vectorially with thermal, shrinkage and tolerance components, rather than taking a single maximum. At the skewed re-entrant corner, the two wings’ movement directions won’t align with the joint everywhere, so check the dowel’s allowed lateral and rotational capacity and edge clearances under the worst combination. Also confirm that slab edge beams, cladding restraints or joint seals do not accidentally provide the restraint the dowels are meant to avoid. Report
Join the conversation
You can post now and register later. If you have an account, sign in now to post with your account.