November 22, 20251 yr comment_620 I encountered an issue with reinforcement installation on a construction site and there was a discussion regarding the following detail:In first drawing, the top reinforcement mesh is placed on top of the U bars, while in another drawing it is below the U bars, meaning the U bars hold both the top and bottom mesh.Is it critical how this detail is executed?Can the top mesh be placed on top of the U bars, or does it need to be under the U bars?Is it sufficient to ensure the proper overlap of bars only?The design standard being followed is Eurocode 2 (EC2). Report
Tuesday at 08:54 AM4 days comment_639 It can be critical, but not simply because one drawing shows the mesh over the U-bar. Under EC2 what matters is that the top bars retain the specified concrete cover, effective depth and edge anchorage/lap, and stay tied in position during casting. If the U-bar is intended to anchor or enclose the top mesh, the top bars should normally sit inside/below its horizontal leg with the required lap; placing them above may still be acceptable if cover and effective depth are checked and the bar is positively tied. Overlap alone is not sufficient; raise an RFI/shop-drawing clarification. Report